Modbus RS485 - good data back but the code is not picking it up

I have sniffed the data to and from the M21+ and i have valid data going out and coming back but the M21+ is not recognizing it.  I have attached what is basically the example code. Can anyone see anything wrong with the Rx portion?

I am on Z and Y and have half duplex switch set to on.  again validated i have a good modbus string leaving and coming to the M21+. 

sniffed data


SENT - 01 03 00 05 00 03 15 CA

Returned - 01 03 06 00 00 00 44 00 00 61 60



At this point this if statment is not firing:   " if (modbus.isWaitingResponse())  "


----------------------------------------------------------------------------code


#include <ModbusRTUMaster.h>


// Define the ModbusRTUMaster object, using the RS-485 or RS-232 port (depending on availability)

#include <RS485.h>

ModbusRTUMaster modbus(RS485);



uint32_t lastSentTime = 0UL;

const uint32_t baudrate = 9600;

bool Dig1State = 0;


////////////////////////////////////////////////////////////////////////////////////////////////////

void setup() {

  Serial.begin(9600UL);

  Serial.println("Modbus starting...");

  


  // Start the serial port


  RS485.begin(baudrate, HALFDUPLEX, SERIAL_8N1);



  // Start the modbus master object.

  // It is possible to define the port rate (default: 38400)

  modbus.begin(9600);


  pinMode(Q0_1, OUTPUT);

  delay(2000);

  

  Serial.println("Loop start...");

}


////////////////////////////////////////////////////////////////////////////////////////////////////

void loop() {

  // Send a request every 1000ms

  if (millis() - lastSentTime > 2000) {

    

    Dig1State = !Dig1State;

    digitalWrite(Q0_1, Dig1State);

    

    Serial.println("Modbus poll...");

    // Send a Read Coils request to the slave with address 1

    // It requests for 23 coils starting at address 10

    // IMPORTANT: all read and write functions start a Modbus transmission, but they are not

    // blocking, so you can continue the program while the Modbus functions work. To check for

    // available responses, call master.available() function often.

    modbus.readHoldingRegisters( 1 , 5, 3);



    lastSentTime = millis();

  }


  // Check available responses often

  if (modbus.isWaitingResponse()) {

    ModbusResponse response = modbus.available();

    if (response) {

      Serial.println("Modbus responce...");

      if (response.hasError()) {

        // Response failure treatment. You can use response.getErrorCode()

        Serial.print("Modbus Comm Error");

      } 

      else {

        // Get the coil value from the response

        for (int i = 0; i < 3; ++i) {

          Serial.print(i);

          Serial.print("- ");

          Serial.println(response.getRegister(i));

      }

   }

  }

 }

} //loop


Avatar
Discard
1 Answer
0
Best Answer

Hello friend, 


Maybe the !modbus.isWaitingResponse() is not used in the right situation, you can check it and compare it with this example: https://www.industrialshields.com/blog/arduino-industrial-1/post/communicating-by-modbus-rtu-through-a-rs485-serial-interface-seneca-z-d-in-module-93. Or you can adapt this example and try it directly.


Thank you, 

 